B3IN
bhtedu
Einmalposter
Einmalposter
#1 B3IN
Beitragvon bhtedu » Di 10. Dez 2013, 11:46
Hello, I have a question.
Can connect multiple b3IN in series, using the "I" port?
I have installed 2 or 3 sensors in each B3IN and have problems:
1: Two outdoor pir sensors (12mA)
No work both at once. separated works.
2: 1 water sensor, 1 gas sensor.
I tried to connect a B3IN to another through the "I" port, and one sensor in each b3in. But neither works...
Danksagung erhalten: 6 Mal
#2 RE: B3IN
Beitragvon LuckyLPA » Di 10. Dez 2013, 19:25
Hello and welcome...
[zitat]1: Two outdoor pir sensors (12mA)[/zitat]
12+12=24mA - maximum on B3IN is 25mA ... is almost too much. Try an external power suply. But remember the input contact must be potential free.
[zitat]Can connect multiple b3IN in series, using the "I" port?[/zitat]
u can only use one B3IN on one LCN-Module.
greetings Carsten
#3 RE: B3IN
Beitragvon Uwe » Mi 11. Dez 2013, 00:28
Hi and welcome :D
See also jumper settings in B3IN Instructions (maybe not easy if you got the paper in german)
[zitat]Jumper setting active low (jumper on the left):
When an input against the GND terminal is bridged, the connected module sends the MAKE command.
On opening, comes the BRAKE command.
Jumper setting active high (jumper right):
When the voltage is bridged to an input for the supply voltage, the BRAKE command is sent.
In an open contact input the MAKE command is executed[/zitat]
It must be the same for all contacts, mixed connections are not possible.
Good luck, Uwe
Mitglieder in diesem Forum: 0 Mitglieder und 27 Gäste
